I'm planning to get some colocation space from someone in my area, and like most companies that offer colocation, ask about power supplies (of course) in the quote form.

I'll need a power of 1000W per 4Us.

So, basically I need a 110V-15AMP circuit for each 4Us of hardware. But they offer a maxiumum of 4 circuits; as I'm pretty sure this is a standard, what does it mean? Does it mean I get 1 circuit per U, or 1 circuit per rack?

It would make no sense to just offer one per rack (42Us with just 4*110V-15AMP?!), but I'm unsure exactly what to expect as far as power in a rack in a datacenter.

EDIT:

The servers for colocation are ASIC hardware. To be more specific they're Bitmain AntMiner S2. Each unit takes 4Us, with an integrated PSU that supplies 1000-1100W. So, speaking of space, every rack should be able to contain up to 10 units.

ewwhite
  • 194,921
  • 91
  • 434
  • 799
XCore
  • 167
  • 2
  • 7
  • 3
    I'm pretty sure that they're asking about your power _usage_, not the maximum amount of watts that each of your power supplies can draw. You'll have to dig through your documentation to find this, or make an educated guess.. or get an electrician to measure it for you. – pauska Jun 30 '14 at 09:49
  • 2
    You should ask your provider on how they are gonna cable your rack, this is totally up to them. – MichelZ Jun 30 '14 at 10:35
  • Am I the only one frowning at the idea of calling those things "servers"?!? – Massimo Jun 30 '14 at 17:12

3 Answers3

11

Typically, co-location providers build out the rack electrical on-demand to customer specifications. Due to the variances in provisioning and client requirements, it doesn't make sense to waste the effort of pre-provisioning power until the rack space is sold.

New racks... no power feeds (I had to wait 12 hours for Union electricians) enter image description here

With power!! enter image description here


You seem to have another question about sizing power. What do you mean by 1000W per 4U? You should list the hardware you intend to use in a more understandable form.

  • How many servers do you have?
  • What make/model of server are they?

In terms of power density, data centers are rated for a certain amount of cooling and power per square-area. So unless you're in a high-desity facility, it's likely that you wouldn't be able to fill a rack with servers. You'll run out of power and cooling allotment well before you can fully populate the rack.

Power is traditionally delivered on one or two feeds per rack, and is rated at a certain Amperage. Electrical code typically limits you to the use of 80% of the circuit's limit. The power feeds can be A/B redundant, to which you'd only be able to use 40% of the capacity of each circuit...

But again, you may not even want redundant power or be using equipment with dual power supplies. So this goes back to what you wish to install at the colo. If your servers collectively consume less than 1000W, you can get by with 1 or 2 20A or 30A circuits. Looking at the Netelligent configuration tool, they seem flexible and willing to provide whatever you need.

My colo power utilization graph. I hover at 75% of the circuit's capacity. enter image description here


Edit:

You have a very unique use case in that you'll be using specialized ASIC Bitcoin-mining hardware that has a known power consumption rate.

In this case, I would opt for larger circuits. You'll want 30A circuits, and can possibly run up to three units per circuit. Likely only two per. Real measurements show these running at 8.7A per unit on 110-120V circuits. 208V is an option at the colo, but you'd need to ask the datacenter about their efficiency and how they're providing their 208V.

With four FAT circuits, you could potentially accommodate 10 units, but you'll likely have to buy multiple racks to handle cooling and thermal concerns. I mentioned that colo facilities are rated for a certain density; often 4,000-6,000W/rack.

At this point, tell the potential colo provider exactly what you have and intend to do, and they'll make it happen and give you an accurate outline of cost/space/cooling/power variables.

enter image description here

ewwhite
  • 194,921
  • 91
  • 434
  • 799
  • Thanks for your answer, I just updated my question; do you think they should be able to correctly supply those units? – XCore Jun 30 '14 at 12:27
  • I see... But what would you suggest in terms of quote? How many of those circuits should I consider? Is it X for every rack or unit or...? What does that number mean in a sysadmin slang? @ewwhite – XCore Jun 30 '14 at 12:48
  • @XCore See my edit. You won't get 10 of these in a rack. You will likely need to option more space, since data centers have a cap on the amount of wattage allotted per square foot/meter. – ewwhite Jun 30 '14 at 12:52
  • Just read it, thank you very much! :) Very enlightening! – XCore Jun 30 '14 at 12:52
  • Most colo facilities will permit no more than 2x20A of power in one rack. Contact your specific colo provider for details. City fire ordinances may limit the power as well. For your systems, I would ask the manufacturer what is the expected amp draw and peak load. You will want to provision power such that you have some overhead for switches, out of band management tools etc. Note that most providers want you to stay within 80% of your peak usage so not to trip circuit breakers. – jeffatrackaid Jun 30 '14 at 18:26
  • @jeffatrackaid Untrue (as I'm standing in a colo that has a 6kW limit per rack). The [specific colo provider in the original question is willing to provision up-to 4 x 30A 208V per rack](http://www.netelligent.ca/cartcolo). This a little different than server provisioning, though. We know what the draw of this particular hardware is. It won't fluctuate much. – ewwhite Jun 30 '14 at 18:44
  • I should have said 2x30A 110V. I think that's what we used to have. Don't forget room for a switch (if needed) and out of band tools. The last thing you want is a tripped circuit breaker. Also if you do run near peak, be sure to have your PDU enforce staggered power ups. Nearly any system can cause an amp spike on power-up. – jeffatrackaid Jun 30 '14 at 18:50
4

If you are looking to put 10KW in a single rack, power is only going to be 1 of your worries. Heat Rejection is going to be the other. Rack power is determined by the PDU(s) that are installed in it. if you are starting to pull >1kw per outlet you would probably want High Density PDUs and to feed the antminers 208V as opposed to 110/120V (less amps more volts == smaller wire sizes). Looks like the antminer pulls around 5.2A at 208V. putting 10 of them in a rack would be 52A at 208. Well within range of most Blade Center type PDUS.

Doon
  • 1,441
  • 9
  • 9
  • 2
    +1 for mentioning cooling. Many times the watts-per-square-foot limitation in a datacenter is for cooling more than power distribution. You can usually bring more power to a rack pretty easily (pulling more cables or tapping a second power bus), but you can't take the heat away any faster... – voretaq7 Jun 30 '14 at 17:08
0

When they say there are 4 circuits per rack it just means 4 individual lines of power, probably with individual switches for each line. These are typically wired into Power Distribution Units (PDUs) that branch off into multiple electrical outlets within the rack.

This allows you to distribute your equipment's redundant power supplies over two or more circuits so that if there is a failure (accidental or deliberate) of any one circuit your racked equipment can continue to run on the other redundant power supply.

It's also a way for a power sucking piece of equipment to spread its amp-load over multiple circuits. If you have an 80 amp requirement you can't fulfil that on any one circuit but you can spread that over 4x 30 amps circuits.