8

I've never had an uninterruptible power supply and think of buying one. What not-so-obvious things should I not do to the UPS so that it lives longer?

I don't mean some obvious abuse like dropping/exposing to direct heat/exposing to wrong voltage. I mean less obvious things like its not acceptable to leave an acid battery UPS unplugged for long time after it has been used because some chemical processes start in half-discharged batteries and render the batteries unusable. What other misuses should I know about?

sharptooth
  • 2,727
  • 4
  • 32
  • 38

7 Answers7

4

The SLA (sealed lead acid) batteries in UPSes shouldn't be left in a discharged state. If they are, sulfates will build up on the plates and their capacity will be reduced. This isn't normally a problem in UPSes, since they're always plugged in and after a power outage will charge the batteries back up when the power comes on. But if you somehow decided to unplug a UPS after the batteries were drained and then left it sitting unplugged for a week, you'd probably notice the battery discharging sooner next time.

Ward - Reinstate Monica
  • 12,788
  • 28
  • 44
  • 59
  • APC suggests that if you stop using a UPS, you should disconnect the batteries - and that said batteries will last a long time. – Mei Oct 31 '11 at 15:46
3

Dont overload it. If it has a nice status screen to see the load on it try to keep it below about 60%

By discharging it faster will wear out the the battery faster

Heat, humidity are also bad for it.

SpaceManSpiff
  • 2,547
  • 18
  • 19
3

While in college I was moving some servers from one room to another. They all where on a really old UPS which apparently had less protection circuitry then current UPS equipment. I started by disconnecting all the servers from the UPS and moving those. Then without shutting down the UPS I unplugged it from the wall. Sparks started shooting out of the UPS and it literally started bouncing.

The electronics teacher had a plausible sounding explanation about why something like this would happen given the design of the UPS, but I don't remember enough details to explain it here.

So the moral of the story is this.

  • When there is no load, always turn off the UPS before disconnecting the power.
Zoredache
  • 128,755
  • 40
  • 271
  • 413
2

According to the answers to my question over here, it's a bad idea to have a power strip touch it either upstream or downstream.

chaos
  • 7,463
  • 4
  • 33
  • 49
2

Don't plug a UPS into another UPS (i.e. Daisychaining them).

There's a good discussion on why not to here, or from APC themselves here.

Mark Henderson
  • 68,316
  • 31
  • 175
  • 255
  • 1
    I have a great story about that .... a 6 UPS dasiychain. We had to turn them off to move equipment. Then no one could figure out which one we needed to turn on first ... That was a great day. – Joseph Kern Jun 22 '09 at 10:34
  • 1
    You're not likely to have one, but I have heard stories of people running a ferroresonant (Sola) transformer through a UPS and literally blowing it up. – dmoisan Jul 06 '09 at 17:12
2

If you know you have wonky power (flicker flicker) adjust the sensitivity of the UPS so it doesn't trip for every little flicker. My apartment unit is next to the elevator. I killed a set of batteries in 8 months this way.

dmoisan
  • 447
  • 2
  • 6
1

Your main concern should be heat. Don't cover it with a bunch of stuff. Keep the vents clear, and allow airflow.

Joseph Kern
  • 9,809
  • 3
  • 31
  • 55