Unsure if this is the correct forum. Anyhow, we have had a network installed, using shielded cat 5 cable.

This cable is in the same trunking as the mains power cable.

The electrician says this is fine. The network man says its not.

Who is correct?

Graham

  • Graham, if you give us your locality, perhaps someone can comment on your local building/electrical code. – kmarsh Feb 01 '10 at 13:27
  • Are you SURE it's STP, not UTP? I've heard of STP, but never actually *seen* it! – Mark Henderson Feb 02 '10 at 20:58
  • In regard to whether or not this is the correct site (it's not really a forum), it's sort of on the edge. However, this is the kind of issue we all have to deal with at some stage or other. The fact that there have so far been no votes to close the question suggest that's how others are seeing it as well. – John Gardeniers Feb 03 '10 at 00:17

4 Answers4

6

For safety, the electrician is correct.

For signal integrity, the network man is correct.

kmarsh
  • 3,103
  • 15
  • 22
  • Agree - check also local building regulations which may require power to be trunked seperately. – pjc50 Feb 01 '10 at 13:19
  • Safety, in this case, is usually about how many holes need to be made in the building code mandated "firewalls" that are usually required every X feet to keep a hypothetical fire under control. – Satanicpuppy Feb 01 '10 at 14:51
  • actually from a ssafety aspect this is probably unsafe electrically as I'd suspect that the cat 5 isn't properly bonded to ground so it's theoretically possible to build up enough inducted amps to arc over. – Jim B Feb 01 '10 at 15:40
  • Amps? Do you realize why Twisted Pair is, uh, twisted? – kmarsh Feb 01 '10 at 20:10
  • He's talking about the shield, not the pairs. – chris Feb 02 '10 at 20:41
  • Even then, it's not the current that will cause an arc-over. :) – John Gardeniers Feb 03 '10 at 00:19
  • inducted voltage generally will not produce an arc unless the current is also sufficient. Static electricitly build up all the time and generally dissapates without an arc unless enough voltage and enoug current is available to get it to jump to ground – Jim B Feb 03 '10 at 02:11
  • This is a grounding issue, not a proximity issue. – kmarsh Feb 03 '10 at 13:42
4

As long as the cat-5 was properly shielded and bonded it should theoretically work (although it should have been prohibitively expensive). However this is not recommended pratice and I think doesn't pass tia-607. See "Installing Cat 5"

Mark Henderson
  • 68,316
  • 31
  • 175
  • 255
Jim B
  • 23,938
  • 4
  • 35
  • 58
  • +1 for the expensive part – Mark Henderson Feb 02 '10 at 20:58
  • I don't know what tia-607 is but let's remember that this is a global site and we have absolutely no idea where the OP is, let alone what standards or rules might apply at that location. – John Gardeniers Feb 03 '10 at 00:22
  • Tia is one of (if not THE) global standards org for telco matters. See http://www.tiaonline.org/about/ generally if TIA said no thre is likely a building code that said no – Jim B Feb 03 '10 at 02:14
2

Your local authorities on these matters should always be consulted to see if there are rules covering this situation.

Back when I was an electrician the rules in my part of the world expressly forbade installing power and any kind of communications cable in the same conduit/duct. If placed in the same underground trench there had to be a minimum separation, but I don't recall what that distance was. The purpose was to try to eliminate the chance of mains power being fed into the comms cables in case someone did something stupid, like put a shovel into them. The Phone company (we only had one back then) had similar rules.

From the network side I would advise against it because shielded or not there is still a reasonable chance of inducing spikes into the cable. While that should never be damaging it can certainly affect throughput. The shield is supposed to prevent that from happening but cable shields are seldom completely effective.

John Gardeniers
  • 27,262
  • 12
  • 53
  • 108
1

signal attenuation/interference - network man is correct. Electrician is wrong.

No network cable should be running alongside electric cables....

That is a cowboy job he did...

t0mm13b
  • 160
  • 3
  • 9