I unplugged my running UPS by mistake. The UPS was new so the batteries were fine, also the load was very low. Could it be that the breaking of the ground path lead to the destruction of the UPS? Now it won't turn on and all the fuses I can access externally are not triggered

The UPS is the Eaton Ellipse Eco 1200

Erli
  • 13
  • 4
  • 3
    There's no way for us to know what's wrong with it. Contact the vendor. – joeqwerty Jun 21 '21 at 23:53
  • I know, but I wanted to know if it was a possibility or simply a coincidence – Erli Jun 21 '21 at 23:58
  • You haven't provided the make/model of UPS so we couldn't even hazard a guess. – joeqwerty Jun 22 '21 at 00:05
  • Sorry, I updated the post with the UPS model – Erli Jun 22 '21 at 00:07
  • 3
    A new UPS which isn't defective in some way will just start supplying battery power when it's unplugged. And maybe beep obnoxiously. Normal UPSes do not make loud banging noises. – Michael Hampton Jun 22 '21 at 00:18
  • I read this old thread https://serverfault.com/questions/56999/testing-a-ups-by-unplugging-it-from-the-wall and one of the answer mentioned a bang noise when unplugging the UPS while it was running so now I'm wondering if I broke my UPS because I accidentally unplugged it. – Erli Jun 22 '21 at 00:32

1 Answers1

0

The Short Answer it is DEAD (for the moment), without that, an Electrician was onsite:

You killed your UPS due to a Voltage-over-Fault. (Coil Discharge Ignition)

  • The Main issue and cause is, that you can, even under nearly Zero Load, get and become Voltage Spikes that can kill any Electronics Inside. Specially Capacitors.

  • An Other Reason for this can also a Faulty Production Process, which may be Covered from the Warranty

  • A Third Variant is also Possible, SOME - but, not often of these ones have also a second Fuse, which is only Accessible by opening the CASE of the UPS - Remind, for this action the UPS should stay away from power for at least HOURS - Even then there could be Voltage on the Board!!

  • Remind if this not Solve the Issue, look for a RESET Procedure on your Manual, APC UPS have that kind (usually long-term pressing ON/OFF, but this differs from vendor to Vendor)

  • In Any Case, Check the Warranty of your Device, Claim a Case and replace it.

Remind - NEVER unplug a running UPS, this may lead not only to take damage to itself and can and will (already seen in the past) kill and terminate any Connected Devices to it.

By the way, to explain it with a bit of physics, due to the load on your UPS the current which is flowing, is towing a lighting to the other pole which then Shorten your Circuit and BANG your Electronics :-( (my English sucks to describe that in full perfect English)

With Regards

Electrician and IT Administrator in one Person :-)

i hope i could help ya :-)