I've got an old UPS for which I bought a new battery. The new battery is different in size (longer). Thus it doesn't fit in the structure.
However, if I keep the new battery vertically, I can manage to squeeze it in. But with it tilted, the contacts are not on top anymore (obviously) :)
My question is, if it's safe to keep the battery in this position. We know for example, car batteries shouldn't be used in different angles because of some liquid in it.
So is this ok or are there any threats/dangers?
Thanks!
1if its acid, DON'T! otherwise, have it your way... – tumchaaditya – 2012-06-19T06:44:43.653
1@tumchaaditya Do UPS batteries today have acid in them? – itsols – 2012-06-19T09:49:38.473
i am not aware of that.....that is why i posted previous comment. – tumchaaditya – 2012-06-19T11:59:54.587
1What's the manufacturer and model number on the replacemnt battery? VRLA, SLA, AGM are terms for various sealed lead acid batteries. AGM and VRLA typically have the acid absorbed in fiberglass. Older UPS systems may use Gel, but given the failure due to overcharge and gas pockets in the gel, this is old technology being phased out. Manufacturer's spec sheet will tell you what construction is used for this battery. – Fiasco Labs – 2012-12-20T23:57:32.310